Question: We have spots set-up on the backwall, the person who ran the circuit only put in a 20amp circuit and with all the spots on, it pulls 18amps consistently. Which it trips the breaker when they get shut off and turned back on. Can I run a 30amp circuit to handle the spots, they do plug into a 2g outlet box or do I need to seperate it into 2 20amp circuits?I want things to be safe and meet the code.
Code Requirements
According to the National Electrical Code (NEC), the maximum allowable load for a 20-amp circuit is 80% of its rated capacity, which is 16 amps. In your case, the load is consistently drawing 18 amps, which exceeds the allowable limit.
Options to Address the Problem
Option 1: Run a 30-amp Circuit Installing a 30-amp circuit would provide sufficient capacity for the load. However, you must ensure that: The wiring is rated for 30 amps. The outlet box is compatible with a 30-amp plug and receptacle. The spots are equipped with compatible plugs and cords.
Option 2: Separate into 2 20-amp Circuits Dividing the spots into two circuits would balance the load and prevent circuit overloads. Each circuit would have a dedicated 20-amp breaker and wiring.
Recommendation
Option 2 is generally recommended for the following reasons:
Safety
Dividing the load reduces the risk of electrical fires and shocks.
Flexibility
You can easily adjust the lighting levels by turning on or off individual circuits.
Code Compliance
Splitting into two circuits ensures compliance with NEC requirements for load limits.
Additional Considerations: Check the wattage of each spot and the total load on each circuit. If possible, distribute the spots evenly between the two circuits. Use proper wire gauges and circuit breakers to ensure safe operation. Have the electrical work inspected by a qualified electrician to verify compliance with code and safety standards. Flag for review