User: njtrombley, Location: Massachusetts
Asked on: Tuesday, January 25, 2011 at 9:13 am EST
Answered on: Thursday, May 23, 2024 at 5:16 pm EDT
Question: Hello all, I have a question that came up out in the field that I need some other interpretations on. We are wiring a nuro-care facility, 39 bed, and at each bed there is a medical gas panel that mounts in the wall and it comes complete with 3 - Hospital grade receptacles fed with normal power and 3 - Hospital grade receptacles on a generator panel. Also in the medical gas panel is medical gas (surprising I know). There are gas lines that patients get hooked up to for oxygen etc. These lines are pressurized by a compressor and a vacuum pump. Both the compressor and the vacuum pump are on the generator circuit. The generator is sequenced so that all the loads don't come on at once and stall the generator. The compressor and vacuum pump are part of the generator sequencing process and are delayed to be energized 15 seconds after the generator starts up. The way we did this is we put the compressor and vacuum pump on contactors and we are controlling the coil off the transfer switch because the transfer switch has control wiring that can be delayed. So the generator turns on, the vacuum pump and compressor are off until the transfer switch contacts close which pulls in the contactors for the vacuum pump and compressor.Now, to make a long story longer. The electrical room where the breakers are located for the vacuum pump and compressor are about 200' away from the mechanical room where the vacuum pump and comressor actually sit. We are putting the contactors in the mechanical room where the pump and compressor sit, but do we need a disconnect in front of the contactors in the mechanical room? The equipment has disconnects on them from the factory, but it's not a typical disconnect that would come with a gear package for instance (I will attach a picture). I know that the obvious answer is ask the AHJ, but I would like to know the facts before I do so.
NEC Requirements
NEC 430.112(A)(1): Requires a disconnect at the point of maintenance and servicing for equipment that has a "maintained voltage" of greater than 50 volts. NEC 430.112(B)(1): Defines "maintained voltage" as a voltage that persists for more than 3 minutes after the disconnecting device is opened. NEC 430.112(C)(2): Exempts equipment from the requirement for a disconnect if the disconnecting device is located within sight of the equipment and is capable of being locked in the open position.
Interpretation
The vacuum pump and compressor are likely to have a maintained voltage, as they are powered by a generator and are intended to continue operating during a power outage. The contactors used to control the equipment are not disconnecting devices within the meaning of the NEC. The equipment itself does have disconnects, but it is not clear whether they meet the requirements of NEC 430.112(C)(2), as they may not be visible from the contactors and may not be capable of being locked in the open position.
Conclusion
Based on the provided information, a disconnect is likely required in front of the contactors in the mechanical room. This is to ensure that the equipment can be safely serviced and maintained, as required by NEC 430.112.
Recommendation: Consult with the AHJ to confirm the specific requirements for this installation. Consider installing a disconnect switch that meets the requirements of NEC 430.112(C)(2) in the mechanical room in front of the contactors.* Ensure that the disconnect is visible from the contactors and can be locked in the open position. Flag for review