User: ayoung14, Location: Portage, Indiana NEC: 2008
Asked on: Tuesday, January 25, 2011 at 9:30 am EST
Answered on: Tuesday, May 14, 2024 at 12:44 am EDT
Question: What part of the NEC would require a separate raceway for different owners electrical wiring. We are placing a new circuit into the raceway not owned or controlled by the city owning the streetlight circuit already in place. No separate raceways now.
NEC Article 300.3(C)(1)"Conductors of different systems, such as light and power, signal, and radio, and different circuits of the same system, shall not occupy the same raceway, cable, box, or cabinet; however, conductors of different circuits of the same system that are used to supply the same area shall be permitted to occupy the same raceway, cable, box, or cabinet.Exception: Where conductors of different systems are installed in a manhole, vault, tunnel, or similar underground structure or occupy a space dedicated to electrical purposes only (such as a cable vault, pull box, equipment room, electrical closet, or manhole), all of the following conditions shall be met:(a) The conductors are not in contact with one another.(b) The conductors are securely fastened in place.(c) The conductors are not subject to physical damage." Flag for review