Topic: Nec 517.32(c)(3)
User: anbm, Location: West Virginia, USA NEC: 2020
Asked on: Tuesday, January 25, 2011 at 1:27 pm EST
Answered on: Tuesday, May 14, 2024 at 12:45 am EDT
Question: 2008 NEC 517.32(C)(3) permits HVAC controls to be fed from life-safety branch panels.517.34 still allow HVAC controls to be fed from equipment branch panels.So, is 517.32(C)(3) an option / engineer's choice or we have to comply?
- 32(C)(3) is an option / engineer's choice.517.34 requires HVAC controls to be supplied from equipment branch panels where HVAC equipment is installed. This rule is not modified by 517.32(C)(3). However, 517.32(C)(3) provides an additional option to supply HVAC controls from life-safety branch panels. Therefore, the engineer can choose to supply HVAC controls from either equipment branch panels or life-safety branch panels.