Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: mulitple conductors feeding exhaust fans thru frequency drives causing back feeds

User: littledog, Location: Northern illinois

Asked on: Tuesday, January 25, 2011 at 1:58 pm EST
Answered on: Tuesday, May 14, 2024 at 12:45 am EDT

Question: We have 1-conduit with 6#10 and ground wire for 2 exhaust fansthese are wired thru 2 separate frequency drive units and then to the fanswhen one fan is taken off line there is an 18volt reading from each phase to ground on the disconnected feederWhat can cause this situationHelp please

Possible Causes of 18V Reading from Phase to Ground on Disconnected Feeder



1. Capacitance

The voltage reading may be due to capacitance between the conduit and the electrical wires. When one fan is disconnected, the capacitance forms a path for voltage to flow through, resulting in an 18V reading.

2. Common Neutral

If the frequency drives share a common neutral, the disconnected fan's phase wires may still be connected to the neutral through the other fan's frequency drive. This can create a voltage potential between the phase wires and ground.

3. Induced Voltage

The frequency drives may be generating harmonics or other high-frequency signals that can induce voltage into the conduit. When one fan is disconnected, the harmonic currents may flow through the conduit and cause the 18V reading.

4. Faulty Drive Unit

A failed frequency drive unit may be leaking voltage onto the disconnected feeder. This could result in an 18V reading even when the fan is not connected.

5. Ground Fault

A loose or faulty ground wire may be allowing current to flow back through the conduit and creating the 18V reading.

Troubleshooting Tips



Isolate the fan feeders

Disconnect the feeders from both frequency drives and measure the voltage to ground. If the 18V reading persists, it indicates a problem with the conduit or grounding.

Check the frequency drives

Examine the drives for any signs of damage or loose connections. Ensure that they are properly grounded and not leaking voltage.


Inspect the conduit

Look for any breaks or insulation damage that could cause capacitance or leakage.

Verify grounding

Ensure that the electrical system is properly grounded. Inspect the ground wire connections and verify continuity.


Contact a qualified electrician:
If the issue cannot be resolved through troubleshooting, it is advisable to consult a qualified electrician to further investigate the cause and implement appropriate corrective measures. Flag for review

Previous Question Next Question