Question: I went to a job today where the electrician ran his conduit up to the fireblock and then put a 45 degree angle to avoid the fireblock and go the rest of the way up. This is going to make the conduit part of the sheetrock wall. Is this allowed? Will this maintain the fire rating? I usually see the conduit going through the fireblock and then fire caulk around the penetration.
Generally, the approach described is not allowed per code.
Code Requirements
NEC 300.21
Raceways shall not penetrate fire-resistant-rated walls, floors, or ceilings unless approved.
NFPA 70 (NEC) Table 300.21
Electrical Penetrations of Fire-Rated Assemblies
IBC 708.2.1
Fire-rated assemblies shall be continuous throughout, and their fire resistance shall not be impaired by penetrations, openings, or joints.
Fire Rating Concerns
The 45-degree bend in the conduit creates a potential weak point in the fire-rated assembly. The conduit itself, if not properly sealed, can act as a pathway for fire to spread through the fireblock.
Allowed Methods
Fire-Rated Penetrations
The conduit should pass directly through the fireblock, with appropriate fire caulk or other approved methods used to seal the penetration and maintain the fire rating.
Protected Openings
If a penetration through the fireblock is unavoidable, a protected opening can be created using fire-rated materials such as sleeves or collars to maintain the fire integrity.
Consequences of Non-Compliance
Failure to maintain the fire rating of a fireblock can create a significant fire hazard. The building inspector may require the installation to be corrected. It can compromise the safety of the building occupants and property.
Recommendation:
It is recommended to have the electrician correct the installation by routing the conduit through the fireblock and sealing the penetration appropriately. This will ensure compliance with code requirements and maintain the intended fire protection for the building. Flag for review