Question: The 2008 code code book says GFI protection is required for boat hoists not exceeding 240 volts. In the handbook it goes into further detail about only circuits that are 15 or 20 amps. So what do you go by the handbook or the code book. Case in point I wired a boat lift with a 30 amp 2-pole breaker which is what was called for. I was turned down because it was not a gfi. the code book says not exceeding 240 volts. i argued the handbook differs and says only 15 and 20 amp. This is a home and not commercial work. Thanks in advance

The National Electrical Code (NEC) is the prevailing document and supersedes any information in the handbook. The NEC requires GFI protection for boat hoists not exceeding 240 volts.

Relevant Code Section

*

NEC 2008, Section 555.3
- Ground-Fault Circuit Interrupters (GFCIs).

Code Interpretation

The code language "not exceeding 240 volts" encompasses all circuits up to and including 240 volts. Therefore, GFI protection is required for boat hoists with circuits of any amperage, including 30 amps.

Conclusion:


Despite the differing information in the handbook, the NEC requires GFI protection for all boat hoists not exceeding 240 volts, regardless of amperage. The 30-amp boat lift circuit you installed should have been protected with a GFI device to comply with the NEC. Flag for review