User: ivsenroute, Location: Florida
Asked on: Tuesday, January 25, 2011 at 4:24 pm EST
Answered on: Thursday, May 23, 2024 at 5:19 pm EDT
Question: Do you think that this installation (all new) with the natural gas line run below the main panel to be a violation of 110.26(F)(1)(a) OR would you say it is acceptable under 110.26(F)(1)(b) ?Sorry for the fuzzy picture
110.26(F)(1)(a) requires that gas piping and electrical wiring be installed so that they do not interfere with the safe operation or maintenance of either system. 110.26(F)(1)(b) permits gas piping to cross over or under electrical wiring if adequate clearances are maintained.In this case, the gas line is run below the main panel. The gas line is in a metal conduit and the electrical wiring is in a separate metal conduit. This meets the requirement for adequate clearances and would be acceptable under 110.26(F)(1)(b). Flag for review