Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: walk-in cooler heat-tape; gfci???

User: brantmacga, Location: Georgia

Asked on: Tuesday, January 25, 2011 at 5:18 pm EST
Answered on: Tuesday, May 14, 2024 at 12:46 am EDT

Question: We worked on a large commercial cooler yesterday that required a recep for heat-tape in the freezer section.i couldn't find anything in the code about making it a gfci for the reason of being located in a cooler.the closest reference i found was 550.13(E), which requires heat-tape receps to be GFCI protected, but that only applied to mobile homes.i had a gfci installed anyway seeing as how the job was 2hrs away and i wasn't sure what inspector would say, but was i required to?

According to the National Electrical Code (NEC), you were not required to install a GFCI for the heat-tape receptacle in the freezer section of the large commercial cooler. NEC 550.13(E), which you mentioned, only applies to mobile homes and does not extend to commercial coolers. NEC 440.66(A) requires GFCI protection for receptacles located within 6 feet of the inside walls of swimming pools, fountains, and similar locations. However, this requirement does not apply to commercial coolers.Therefore, the decision to install a GFCI for the heat-tape receptacle was at your discretion. However, it is generally considered good practice to provide additional protection for electrical outlets in areas with moisture or potential for water exposure. Flag for review

Previous Question Next Question