User: rcampbell, Location: Dallas, Tx
Asked on: Tuesday, January 25, 2011 at 6:35 pm EST
Answered on: Tuesday, May 14, 2024 at 12:46 am EDT
Question: not a big deal... im gonna give in and change the cord. but for future reference, i gotta know. 38.7 A appliance fed from a 50A, 208V, single phase ckt... used 6awg as i was out of 8's. fed it from recep and i made a cord/plug assemnly with 8/3 soow. inspector is questioning this since art. 400 rates 8awg soow at 40 A. he is saying that the cord is not rated to handle the 38.7 X 125%. the unit itself says to supply it with #8awg conductors. what am i missing? this inspector is tough, but reasonable, and i enjoy having these conversations with him, so any insight would be appreciated...
According to Article 400 of the NEC, the ampacity of an 8 AWG SOOW cable is 40 amps. However, the appliance in question requires conductors rated for 38.7 amps, which is within the ampacity of the 8 AWG SOOW cable.The inspector may be concerned about the 125% rule, which requires that the ampacity of the cord be increased by 25% if it is used in a continuous load application. However, the appliance in question is not a continuous load, as it is not expected to operate at its full rated load for an extended period of time.Therefore, the 8 AWG SOOW cable is adequately rated for the appliance in question, and the inspector's concerns are unfounded. Flag for review