User: delsol, Location: Tennessee
Asked on: Tuesday, January 25, 2011 at 9:03 pm EST
Answered on: Tuesday, May 14, 2024 at 12:46 am EDT
Question: I am about to estimate a job and have a bonding question.The existing service consists of a 400 amp meter can with extra lugs for serving multiple panels. Currently, there are two panels served from the meter can (A 200 amp and a 100 amp panel, both interior) The meter can is directly behind the two interior panels, separated only by a 2x4 wall. I will be installing a 200 amp panel (exterior), which will serve the existing 100 amp panel and a new outbuilding. The grounding electrode conductors from the water main and ground rod enter the existing 200 amp panel.My plan is to install a main bonding jumper from this existing panel to my new exterior load center. (The existing 100 amp is bonded to the existing 200 amp panel.) My interpretation is that this is one central service with multiple enclosures. Does anyone have any thoughts on this?
Your plan is generally correct.Interpretation
The existing setup can be considered as one central service with multiple enclosures, as all panels share a common grounding system. The main bonding jumper you propose will ensure that all enclosures are adequately bonded.
Grounding Electrode Conductors
The grounding electrode conductors entering the existing 200 amp panel should be connected to a single grounding electrode conductor that extends to your new exterior load center. This ensures that all enclosures have a path to earth ground.
Main Bonding Jumper
Install a main bonding jumper between the existing 200 amp panel and your new exterior load center. The jumper should be sized according to the largest service-rated conductor entering the enclosure. (In this case, it would be sized for a 400 amp conductor.)
Additional Considerations
Ensure that all electrical connections are made securely and in accordance with applicable codes. Inspect the existing grounding system and make any necessary repairs or upgrades to ensure its integrity.* Obtain a permit from your local building department before starting any work.
Conclusion:
Your plan to install a main bonding jumper from the existing 200 amp panel to your new exterior load center is appropriate for a central service with multiple enclosures. By implementing these measures, you will ensure a safe and compliant electrical installation. Flag for review