Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: X-frmr calculation

User: eager2learn, Location: Mennifee,Ca

Asked on: Tuesday, January 25, 2011 at 11:49 pm EST
Answered on: Tuesday, May 14, 2024 at 12:47 am EDT

Question: I have a 400 amp buss that is a 3 phase 4 wire system rated for 277/480 volts. This application is suppose to feed a 150kva step down transformer = 480-120/208 volts 3 phase 4 wire. I'm having diffuculties trying to figure out the feeder conductors aswell as over current protection for this particular installation. Where do I start?

Calculating Feeder Conductor Size

Step 1: Calculate the load current: Load current (IL) = Apparent power (S) / Per-phase voltage (V) S = 150 kVA V = 480 volts (1 phase) IL = 150,000 VA / 480 V = 312.5 A Step 2: Determine the number of feeder conductors: 3 phases + neutral = 4 conductors Step 3: Select the appropriate conductor size using an ampacity table. The NEC recommends using THHN/THWN-2 conductors. For 312.5 A, the minimum conductor size is 350 kcmil THHN.

Calculating Overcurrent Protection

Step 1: Determine the maximum overcurrent protection: For 400 amp buss, the maximum fuse rating is 400 amps. Step 2: Select the appropriate fuse or circuit breaker for the feeder conductors: The fuse or circuit breaker rating should be equal to or less than the conductor ampacity. For 350 kcmil THHN conductors, the maximum fuse rating is 400 amps.

Additional Considerations



Grounding System

Ensure that the transformer is properly grounded to prevent electrical hazards.

Conduit or Cable Tray

Determine the appropriate method for running the feeder conductors and provide adequate support and protection.


Connections

Ensure that all connections are properly made and tightened.*

Labeling

Label the feeder conductors and overcurrent protection devices for easy identification.

Note:
It is highly recommended to consult with a licensed electrician or electrical engineer for proper installation and verification of the electrical system. Flag for review

Previous Question Next Question