Question: I have a 400 amp buss that is a 3 phase 4 wire system rated for 277/480 volts. This application is suppose to feed a 150kva step down transformer = 480-120/208 volts 3 phase 4 wire. I'm having diffuculties trying to figure out the feeder conductors aswell as over current protection for this particular installation. Where do I start?
Calculating Feeder Conductor Size
Step 1: Calculate the load current: Load current (IL) = Apparent power (S) / Per-phase voltage (V) S = 150 kVA V = 480 volts (1 phase) IL = 150,000 VA / 480 V = 312.5 A Step 2: Determine the number of feeder conductors: 3 phases + neutral = 4 conductors Step 3: Select the appropriate conductor size using an ampacity table. The NEC recommends using THHN/THWN-2 conductors. For 312.5 A, the minimum conductor size is 350 kcmil THHN.
Calculating Overcurrent Protection
Step 1: Determine the maximum overcurrent protection: For 400 amp buss, the maximum fuse rating is 400 amps. Step 2: Select the appropriate fuse or circuit breaker for the feeder conductors: The fuse or circuit breaker rating should be equal to or less than the conductor ampacity. For 350 kcmil THHN conductors, the maximum fuse rating is 400 amps.
Additional Considerations
Grounding System
Ensure that the transformer is properly grounded to prevent electrical hazards.
Conduit or Cable Tray
Determine the appropriate method for running the feeder conductors and provide adequate support and protection.
Connections
Ensure that all connections are properly made and tightened.*
Labeling
Label the feeder conductors and overcurrent protection devices for easy identification.
Note: It is highly recommended to consult with a licensed electrician or electrical engineer for proper installation and verification of the electrical system. Flag for review