User: jarilu422, Location: S.W. Florida
Asked on: Wednesday, January 26, 2011 at 12:05 am EST
Answered on: Tuesday, May 14, 2024 at 12:47 am EDT
Question: I have a situation. I work for a pool heating/AC/ Electrical company that installs Geothermal water source heat pump. I have a job that the inspector has failed because we ran a new service for the geo heat pump system. He said "could not put more than one service on a building". We did not put the new service on the building, we put it on a banjo pole 40 feet from the building. We do not have any branch circuits from the new service that run into the building. Our service is strictly for the pool heating system. The reason why we did not upgrade the existing service was, the utilities X-form was over loaded. It would have been around $8,000.00 extra. We have done jobs like this in the past in the same municipality and it never has been a problem.Can someone please give me some pointers. If we are in the wrong. If i got a fighting chance. I know he is the AHJ. Dose art. 230.2.(C)(2) come in to play? It is a single phase installation. Is there anything in 680 that I may have mist? Dose all the pool equipment need to be on the same service or panel?
Can the Inspector Legally Fail the Installation?
The inspector's decision to fail the installation due to the new service is questionable. National Electrical Code (NEC) requirements must be followed, but the inspector also has the authority to determine how they apply in specific situations.
NEC Article 230.2(C)(2)
Article 230.2(C)(2) allows for multiple services for a single building if each service: Is separately metered and identified Provides power only to the specific equipment or appliances it serves Meets the requirements of Article 230.2(B) (overcurrent protection, etc.)Your Situation The new service is separately metered and identified. It only provides power to the pool heating system (not the building). It meets the overcurrent protection requirements.Based on these facts, you have a strong case under Article 230.2(C)(2).
Article 680
Article 680 does not specify that all pool equipment must be on the same service or panel. It only requires that pool equipment be properly installed and protected against electrical hazards.
Inspector's Interpretation
The inspector's interpretation that only one service can be used for a building is likely based on local ordinance or practice. However, it is not supported by the NEC.
Fighting Chance
You can appeal the inspector's decision by: Requesting a review by the electrical board or code review committee Submitting a written explanation of how your installation meets the NEC requirements Providing evidence of similar installations that have been approved in the past Emphasizing the safety and practicality of your designPossible Compromises
You could consider the following compromises to address the inspector's concerns: Install an isolating device at the point where the new service connects to the existing infrastructure. Label the new service clearly to indicate that it is only for the pool heating system.* Provide documentation showing that upgrading the existing service would be impractical or cost-prohibitive. Flag for review