Question: I am running (3) 3 phase, 208V, 60amp circuits in the same 2" conduit (5' in length) from a power panel to a JB, then (3) 3/C#6 MC cables from the JB to the end of line devices. The total length of the run is 75'. Can I utilize the exception in section 310.15(A)(2) and not have to derate my conductors. Each load is rated at 45amps. I propose to use 60amp CBs for each load.
Yes, you can utilize the exception in 310.15(A)(2) and not derate your conductors.Explanation
Section 310.15(A)(2) allows for conductors to be installed in a raceway without derating if the conduit is not used to its full capacity and the ambient temperature does not exceed 86°F (30°C). In your case, the conduit (2 inches) is not fully occupied (50% fill = 3.14 sq. in. vs. 6.28 sq. in. available) and the ambient temperature is assumed to be normal (not exceeding 86°F). Therefore, you do not need to derate your conductors.
Additional Considerations
The 3/C#6 MC cables must be properly protected from physical damage and supported every 4 feet.* The circuit breakers must be sized in accordance with Article 210 for the load rating (45 amps). In this case, 60-amp circuit breakers are appropriate.
Conclusion:
Based on the provided information, you can utilize the exception in Section 310.15(A)(2) and not derate your conductors for the described electrical installation. However, it's important to ensure that all other applicable code requirements are met for proper safety and operation of the circuit. Flag for review