User: papa, Location: South Carolina
Asked on: Wednesday, January 26, 2011 at 11:10 am EST
Answered on: Tuesday, May 14, 2024 at 12:48 am EDT
Question: Had a service call at a floating dock yesterday, turns out utility had lost one leg to service. Looked at installation while there see any problems?100 amp. 240/ 120 mlo panel mt. on ramp to floating dock, powered by 3 wire use feeder from service , grd. rod driven at ramp , neutral bar isolatedpanel has five 30 amp gfci s/p breakers suppling power to five pedetals on float via 8/3 rubber cord in sealtite flex, down under water and up to ped.pedestals have 1 light , 2 gfci 120 v, 20 amp recp. all protected by 2, 20 amp. built in breakersramp and float are alum.
Potential Issues with the Floating Dock Electrical Installation
Insufficient Grounding
The ground rod at the ramp may not be adequate to provide a reliable ground path. Additional grounding may be necessary, such as buried copper conductors or multiple ground rods.
Isolated Neutral Bar
Isolating the neutral bar can create a potential shock hazard. The neutral conductor should be properly bonded to the grounding system at the service entrance.
Use of Rubber Cord Underground
The use of rubber cord for the feeder from the panel to the pedestals is not recommended for underground installations. It should be replaced with a properly rated underground cable.
Sealtite Flex Not Properly Sealed
Sealtite flex must be properly sealed at both ends to prevent water ingress. Ensure that the seals are tight and intact.
Pedestal Receptacles Not GFCI Protected
The receptacles in the pedestals should be GFCI protected to prevent shock hazards from ground faults.
Lack of Bonding between Ramp and Float
The aluminum ramp and float should be bonded together to ensure a continuous grounding path. This can be achieved by using a bonding lug or other approved method.
Floating Dock Not Connected to Shore Ground
The utility power should be connected to a grounding electrode system at the service entrance. This grounding electrode system should also be connected to the floating dock to ensure proper grounding.
Recommended Actions: Install additional grounding rods if necessary. Bond the neutral bar to the grounding system at the service entrance. Replace the rubber cord underground with a properly rated underground cable. Properly seal the Sealtite flex at both ends. Install GFCI receptacles in the pedestals. Bond the ramp and float together.* Ensure that the floating dock is connected to the shore grounding electrode system. Flag for review