Topic: Uffer ground

User: kentriolinda, Location: Massachusetts

Asked on: Wednesday, January 26, 2011 at 1:09 pm EST
Answered on: Tuesday, May 14, 2024 at 12:48 am EDT

Question: I recently did a panel upgrade and inspector is requiring a uffer ground. Inspector says it has to be incased in concrete 12 " deep. I looked at 250.52 A-3 and it only states that it must be 20' bare copper ecased in 2" of concrete but I can't find anything where it states the depth it must be. My question is can I remove a portion of the sidewalk and put it in the new portion being that will only be 6" deep?

NEC 250.52(A)(3) states that the grounding electrode shall be at least 20 feet long if installed horizontally, and shall be buried at least 2 feet deep. If less than 20 feet long, all of the electrode shall be below grade.In your case, if you install the Ufer ground in the new portion of the sidewalk, only 6 inches deep, it would not meet the NEC requirement of being buried at least 2 feet deep. Therefore, you cannot remove a portion of the sidewalk and install the Ufer ground in the new portion.You could consider other grounding methods that do not require excavation, such as a ground rod or a cold water pipe. Flag for review