User: erickench, Location: Brooklyn, NY
Asked on: Wednesday, January 26, 2011 at 1:44 pm EST
Answered on: Tuesday, May 14, 2024 at 12:49 am EDT
Question: There are two things about this NEC section that puzzles me. First, NEC 690.8(A)(1) states:The maximum current shall be the sum of parallel module rated short-circuit currents multiplied by 125 percent.Since when is maximum current higher than short circuit current? I would've thought that the nameplate current is the maximum current and the short circuit current would be higher.Second, NEC 690.8(B)(1) states the following:The circuit conductors and overcurrent devices shall be sized to carry not less than 125 percent of the maximum currents as calculated in 690.8(A).If we were to assume that the maximum current is 125 percent of the so called short-circuit current(or nameplate current) then we would be applying the 125% factor twice in performing the calculation. Here's what I mean:short-circuit current multiplied by 125% and then multiplied again by 125% to obtain the conductor ampacity and OCPD rating.Has anyone ever seen the nameplate of a PV module? Does the nameplate designate it as a short-circuit or maximum current? Anyone?
First Puzzle
The term "maximum current" in NEC 690.8(A)(1) refers to the maximum current that the module can produce under fault conditions, which is typically higher than the nameplate current. This is because faults can cause the module to produce higher currents than it is rated for under normal operating conditions. Therefore, the 125% factor in NEC 690.8(A)(1) is applied to the rated short-circuit current to account for this potential increase.
Second Puzzle
The 125% factor in NEC 690.8(B)(1) is applied to the maximum current (as calculated in 690.8(A)) to ensure that the circuit conductors and overcurrent devices can withstand the maximum current that the photovoltaic system can produce. This is to prevent damage to the system and ensure safety. However, it is important to note that the 125% factor is not applied twice to the same current value. The first application (in 690.8(A)) is to determine the maximum current, and the second application (in 690.8(B)) is to size the conductors and overcurrent devices based on that maximum current.
PV Module Nameplate
PV module nameplates typically indicate both the rated current and the rated short-circuit current. The rated current is the current that the module is designed to produce under normal operating conditions, while the rated short-circuit current is the maximum current that the module can produce under fault conditions. Flag for review