User: pjoseph, Location: Brooklyn, NY
Asked on: Wednesday, January 26, 2011 at 1:51 pm EST
Answered on: Tuesday, May 14, 2024 at 12:49 am EDT
Question: I am trying to find out if the fire pump breaker can be in the same cubical with other life safety distribution breakers, or does it have to be in its own cubicalThis is for paralleing gear in a hospital.thanks
NFPA 99: Health Care Facilities CodeSection 6.3.
9.5.4.3 Fire Pump Power Distribution EquipmentThe power distribution equipment for the fire pump shall be located in a separate room, vault, or enclosure dedicated to that purpose and accessible only to authorized personnel.
Interpretation:
The fire pump breaker must be in a separate enclosure from other life safety distribution breakers. Flag for review