Question: Two separately metered services (separate SEC's off a common service drop); however, a grounding conductor connects the 2 panels. Is this legit (install is ca. 1975).http://i15.photobucket.com/albums/a352/TonyPE/IMGP0600.jpg
This is not legit. If the two separately metered services are intended to be service the same building or structure, and the panels are connected by a grounding conductor, the connected panels must be bonded together with a bonding jumper sized per NEC 250.102 (D). Flag for review