User: lec2694, Location: Iuka MS

Asked on: Wednesday, January 26, 2011 at 3:18 pm EST
Answered on: Thursday, May 23, 2024 at 5:22 pm EDT

Question: Does the NEC require a disconnecting device on the outside wall of a residence, when the residence has a undeground electrical supply from a power company riser pole (which the power pole has no means of disconnect and the metering is of the instrument type)?

Yes, the NEC requires a disconnecting device on the outside wall of a residence, even when the residence has an underground electrical supply from a power company riser pole with no means of disconnect and instrument-type metering.

NEC 230.70(A)(1) states:"For each separately metered service and for each feeder supplying a complete dwelling unit, there shall be one or more disconnecting means installed in a readily accessible location outside the building."This requirement applies to all residences, regardless of the type of electrical supply or metering used. The purpose of the disconnecting device is to allow the homeowner or utility to safely disconnect the electrical power to the residence for maintenance or emergency purposes.In this case, the power company riser pole does not have a means of disconnect, so a disconnecting device must be installed on the outside wall of the residence. This device can be a main breaker or fused disconnect switch, and it should be located in a readily accessible location, such as near the electrical meter. Flag for review