Question: Question!210.62 states that we must have one receptacle within 18" the top of the show room window for each 12 linear ft of show window.Does this mean we need this receptacle mounted in the ceiling? Seems like a waste to mount all of these receptacles in the ceiling vs mounting them in a floor box.
The code does not specify where the receptacle must be located, only that it must be within 18 inches of the top of the showroom window. Therefore, it is acceptable to mount the receptacle in the ceiling, on the wall, or in a floor box, as long as it meets the other requirements of the code.However, it is important to consider the practical implications of mounting the receptacle in the ceiling. For example, if the ceiling is high, it may be difficult to reach the receptacle to plug in appliances or devices. Additionally, if the ceiling is not finished, it may be necessary to install a junction box to support the receptacle, which could add to the cost and complexity of the installation.For these reasons, it is often more practical to mount the receptacle in a floor box. This will make it easier to access the receptacle and will not require any additional work to install a junction box. Flag for review