Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Voltage @ water lines

User: jotw, Location: Texas

Asked on: Wednesday, January 26, 2011 at 3:52 pm EST
Answered on: Thursday, May 23, 2024 at 5:25 pm EDT

Question: Good afternoon! I have a customer who has complained about being shocked when they turned on the spigot outside. Sure enough, I am reading anywhere between .4 volts - 1.5 volts. Of course, I can't feel that. Nonetheless, there is voltage. Maybe more at times. I don't know.Upon further inspection I discovered that the two subpanels inside the building have the neutrals and grounds bonded together. I thought, "A-ha! I either have a neutral backfeeding that voltage to the cold water ground or I have a ground loop." Then I discover that there is no grounding system whatsoever. Unless there is a uffer (slab ground) in the meter can, there is nothing, and no cold water ground that I can find.So, next decided to go ahead and separate all grounds and neutrals in the subpanels. I ran appropriately sized EGCs to both subpanels, ran a ground from the hose bib to the service, and drove a ground rod. At some point during all of this, I checked for voltage between one of the subpanel EGCs and a ground on a branck circuit (I actually checked three different branch circuit grounds, and one of those was a multi wire branch circuit that I ran the day before). I was reading 40-55 volts to ground on each of those grounds. The thing is, though, is that whoever wired this building cut most of the grounds on the load end. What a mess.Anyway. I continued with the grounding of the service and subpanels kind of hoping that it would go away or fix itself. I finished with grounding all of the service equipment/panels. I'm not getting that 40-50Volts anymore, but, I still have the .4- 1.5 Volts on the water lines. The only time it goes away is when I open the main disconnect breaker. I have also tested the messenger wire from the utility transformer to my ground rod and I get nothing. I am rebuilding the service tomorrow, and I'm hoping that will shed some light on what is happening.Any thoughts on what is happening here? I'm perplexed with the .4-1.5 volts and totally blown away with the 40-50V reading on the branch circuit grounds. Thanks for any helpful input. Or otherwise.

Possible Causes of Voltage on Water Lines



Neutral-to-Ground Fault

A neutral-to-ground fault within the electrical system can cause voltage to backfeed onto the water lines connected to the ground.


Inductive Coupling

The power lines running alongside or near the water lines can induce voltage onto them.

Ground Loop

A ground loop occurs when electricity flows through the ground instead of the intended electrical path, resulting in voltage being present on metal surfaces, including water lines.

Potential Causes of 40-50V on Branch Circuit Grounds



Floating Neutral

A floating neutral occurs when the neutral wire in the service entrance is not properly connected to the ground, causing voltage to be present on the circuit grounds.

Open Ground

An open ground wire in the system can lead to voltage being present on the circuit grounds.

Troubleshooting Steps



Check the Service Entrance

Ensure that the neutral and ground wires are not bonded together. Inspect the service entrance conductors for any damage or loose connections. Test for neutral-to-ground faults using a continuity tester.

Inspect the Electrical System

Look for any loose ground connections on outlets, switches, and appliances. Inspect the wiring for any damaged or disconnected wires.

Isolate the Source

Turn off all non-essential circuits to isolate the source of the voltage on the water lines. Test for voltage on the water lines after each circuit is turned off until the voltage drops. If the voltage persists with all circuits off, it may be originating from outside the building or from the utility grid.

Contact the Utility

If you cannot identify the source of the voltage, contact the utility company to report the issue and have them investigate. They may need to check the transformer and distribution system.

Additional Considerations



Lightning Strike

A recent lightning strike can damage the grounding system and cause voltage to appear on the water lines.


Faulty Ground Rod

Ensure that the ground rod is properly installed and has a low resistance to earth.

Water Heater

The water heater could be grounding to the water lines, causing voltage to appear on them.

Safety Precautions:
Always use proper safety gear when working on electrical systems. Do not touch metal objects while standing on wet surfaces. If you are not comfortable troubleshooting electrical issues, it is best to contact a qualified electrician. Flag for review

Previous Question Next Question