User: erickench, Location: Brooklyn, NY
Asked on: Wednesday, January 26, 2011 at 9:30 pm EST
Answered on: Tuesday, May 14, 2024 at 12:50 am EDT
Question: Okay here's another doozy that I would like to share with you guys as I get my proposals ready. The above exception seem's to be in conflict with the OCPD/Ampacity rules of NEC 690.8(B). It states the following:(b) The short-circuit currents from all sources do not exceed the ampacity of the conductors or the maximum overcurrent size specified on the PV module nameplate.Now here's my argument:Part (b) of this exception permits a code user to ignore the ampacity and overcurrent protection rules in NEC 690.8(B). It is already a given that conductor ampacites and overcurrent protection must be sized at a minimum that is well above the module rated short-circuit current in accordance with NEC 690.8(B). Also, the maximum OCPD nameplate rating is always going to be much higher than the module rated short-circuit current, so this is also a given. If the ampacity is somewhere between the module rated short-circuit current and the values calculated in NEC 690.8(B)(2) this would be a violation of that NEC section. If the ampacity is somewhere between the maximum OCPD nameplate rating and the values calculated NEC 690.8(B)(2) this would be in compliance with that section because conductor ampacity must not be less than the OCPD rating as calculated in NEC 690.8(B)(1) unless NEC 240.4(B) would apply. However, in both cases overcurrent protection is still required by NEC 690.8(B)(1).So tell me what you guys think.
The exception in question allows for the use of conductors with ampacities less than the maximum overcurrent size specified on the PV module nameplate, provided that the short-circuit currents from all sources do not exceed the ampacity of the conductors. This exception is intended to allow for the use of smaller conductors in certain applications, such as when the PV system is connected to a grid-tied inverter that provides overcurrent protection.However, it is important to note that the exception only applies to the ampacity of the conductors, not to the overcurrent protection requirements. Overcurrent protection is still required by NEC 690.8(B)(1), and the overcurrent protective device must be sized in accordance with NEC 690.8(B)(2).In your example, if the ampacity of the conductors is somewhere between the module rated short-circuit current and the values calculated in NEC 690.8(B)(2), then this would be a violation of NEC 690.8(B). This is because the ampacity of the conductors must not be less than the OCPD rating as calculated in NEC 690.8(B)(1), unless NEC 240.4(B) would apply. However, NEC 240.4(B) does not apply to PV systems, so the ampacity of the conductors must be at least equal to the OCPD rating.In conclusion, the exception in NEC 690.8(B) does not conflict with the overcurrent protection requirements in NEC 690.8(B). Overcurrent protection is still required, and the overcurrent protective device must be sized in accordance with NEC 690.8(B)(2). Flag for review