Topic: Therapeutic tub receptacles

User: RND4life, Location: Spokane, Washington

Asked on: Thursday, January 27, 2011 at 12:02 pm EST
Answered on: Tuesday, May 14, 2024 at 12:50 am EDT

Question: How close to a non-powered therapeutic tub can a receptacle be installed in a SPA facility? My enterpretation is that they have to be 6' from the inside wall of the tub based on the code references below.680.2 Definitions, Permanently Installed Swimming, Wading, Immersion and Therapeutic Pools. Those that are constructed in the ground or partially in the ground, and all others capable of holding water in a depth greater than 1.0 m (42 in.), and all pools installed inside of a building, regardless of water depth, whether or not served by electrical circuits of any nature.680.61 Permanently Installed Therapeutic Pools.Therapeutic pools that are constructed in the ground, on the ground, or in a building in such a manner that the pool cannot be readily disassembled shall comply with Parts I and II of this article.680.22 (A) Receptacles.(2) Other Receptacles, Location. Other receptacles shall be not less than 1.83 m (6 ft) from the inside walls of a pool.

Receptacles must be installed at least 6' from the inside wall of a non-powered therapeutic tub in a SPA facility, according to the code references you provided. This is because the tub is considered a "permanently installed therapeutic pool" under the definition in 680.2, and therefore must comply with the requirements for such pools in 680.
61. The requirement for receptacles to be at least 6' from the inside walls of a pool is found in 680.22(A)(2). Flag for review