Question: How close to a non-powered therapeutic tub can a receptacle be installed in a SPA facility? My enterpretation is that they have to be 6' from the inside wall of the tub based on the code references below.680.2 Definitions, Permanently Installed Swimming, Wading, Immersion and Therapeutic Pools. Those that are constructed in the ground or partially in the ground, and all others capable of holding water in a depth greater than 1.0 m (42 in.), and all pools installed inside of a building, regardless of water depth, whether or not served by electrical circuits of any nature.680.61 Permanently Installed Therapeutic Pools.Therapeutic pools that are constructed in the ground, on the ground, or in a building in such a manner that the pool cannot be readily disassembled shall comply with Parts I and II of this article.680.22 (A) Receptacles.(2) Other Receptacles, Location. Other receptacles shall be not less than 1.83 m (6 ft) from the inside walls of a pool.
Based on the code references you provided, it appears that a receptacle must be installed at least 6 feet from the inside wall of a permanently installed therapeutic tub in a SPA facility.Code Section 680.2 defines permanently installed swimming, wading, immersion, and therapeutic pools as those that are constructed in the ground or partially in the ground, and all others capable of holding water in a depth greater than 1.0 m (42 in.), and all pools installed inside of a building, regardless of water depth, whether or not served by electrical circuits of any nature.Code Section 680.61 requires therapeutic pools that are constructed in the ground, on the ground, or in a building in such a manner that the pool cannot be readily disassembled to comply with Parts I and II of Article 680.Code Section 680.22(A)(2) states that other receptacles shall be not less than 1.83 m (6 ft) from the inside walls of a pool.Since a therapeutic tub is a type of pool, it would be subject to the requirements of Article 680. Therefore, receptacles must be installed at least 6 feet from the inside wall of a permanently installed therapeutic tub in a SPA facility. Flag for review