Question: If one of the legs on a 3 phase system has a voltage higher than the other two phases how would the line current on that phase compare to the other two phases? Would it be higher on the other two phases. For instance on a 208/120 system if 2 of the phases were 120V L-G and the other phase was 150V L-G would the current be higher on the 150V leg? My guess is that it would be higher.Would it matter weather the load was a wye or delta load?Could it be said that the higher the L-G voltage is on a given phase the highe the curent will be fo a balanced load? Or must you also compare the relationship between the L-L voltages?
Yes, if one of the legs on a 3-phase system has a voltage higher than the other two phases, the line current on that phase will be higher than the other two phases. This is because the line current is proportional to the voltage and inversely proportional to the impedance. In this case, the higher voltage on one phase will cause the line current on that phase to be higher.For instance, on a 208/120 system where 2 of the phases are 120V L-G and the other phase is 150V L-G, the current will be higher on the 150V leg. This is because the higher voltage on the 150V leg will cause the line current on that phase to be higher.It does not matter whether the load is a wye or delta load. The higher line current on the 150V leg will be the same for both types of loads.It can be said that the higher the L-G voltage is on a given phase, the higher the current will be for a balanced load. However, you must also compare the relationship between the L-L voltages to determine the exact amount of current on each phase. Flag for review