Topic: Fire Alarm Panel Battery Trouble

User: big john, Location: Portland, ME

Asked on: Thursday, January 27, 2011 at 6:32 pm EST
Answered on: Tuesday, May 14, 2024 at 12:52 am EDT

Question: I just put in an FSC series fire alarm control panel made by Edwards. When I first turned it on I got a "Battery Trouble" signal. I figured this was because the panel needed to charge the battery to the proper voltage. Left it overnight, and I came back to the same trouble condition, and the battery was also significantly warm.Only three zones on this panel, running 4 smokes. Nothing fancy at all. The battery polarity is connected right. 12V 5AH is the recommended size for this system.The instruction manual simply says that "Battery Trouble" will show up with low or no voltage. This battery has a 13.5 volt charge. I've also swapped a battery from a different panel and had the same problem.I keep trying tech. support but they keep putting me on hold for ages. Any ideas here?-John

Possible Causes



Faulty battery

Replace the battery with a new one of the recommended size (12V 5AH).


Loose connections

Check all battery terminals and wiring connections to ensure they are tight and secure.

Defective panel

Contact Edwards technical support directly to rule out a potential panel issue.


Overcharging

If the battery is too warm, it could be an indication of overcharging. Check the battery voltage; it should not exceed 13.8 volts. If it does, the panel's charger circuit may be faulty.

Excessive load

Ensure that the panel is not connected to more devices or zones than it can handle. Overloading can drain the battery prematurely.

Troubleshooting Steps

1.

Measure the battery voltage

Use a voltmeter to verify that the battery has a sufficient charge (over 12 volts).2.

Check connections

Inspect all battery terminals, wires, and connections for any corrosion, loose contacts, or broken wires.3.

Disconnect the panel

Temporarily disconnect the panel from the power supply to reset it. Once it is reconnected, check if the "Battery Trouble" signal clears.4.

Contact Edwards

If the above steps do not resolve the issue, contact Edwards technical support directly. They may need to provide further assistance or dispatch a technician.

Additional Tips:
Use only the recommended battery size and type. Ensure that the battery is fully charged before connecting it to the panel. If possible, test the battery using a battery tester or charger to confirm its health. Clean the battery terminals regularly to prevent corrosion. Install a battery monitor to track battery voltage and health. Flag for review