User: bran82004, Location: WISCONSIN, USA
Asked on: Thursday, January 27, 2011 at 8:35 pm EST
Answered on: Tuesday, May 14, 2024 at 12:52 am EDT
Question: This test question example was given and doesnt seem to be correct. the only way i can seem to make it work is by using the amp rating they give in the example. but when using the nec flc chart 430.250 the answer i came up with was 77.5A. which would require a #2 xhhw-2 conductor. any explanation would be great thanks..3. A feeder supplies three 460-volt, three-phase, 1740 RPM, Design B, alternating-currentmotors. The motors have the following nameplate ratings: 25 horsepower, 28.4 amperes; 15horsepower, 18.2 amperes; and 10 horsepower, 11.3 amperes. Assuming all the motors areoperating under continuous duty, what minimum size XHHW-2 feeder circuit conductors arerequired to supply the motor load? The conductor terminations are rated at 75?C.Answer 4 AWG NEC 430.6, 430.24, 430.150, 310.16
Explanation of the Correct Answer
The minimum size XHHW-2 feeder circuit conductors required to supply the motor load is
4 AWG, as stated in the answer.
Calculation of Feeder Current (Using NEC 430.250 FLC Chart)
Calculate the Full Load Current (FLC) for each motor using the nameplate amp rating: 25 hp motor: 28.4 A 15 hp motor: 18.2 A 10 hp motor: 11.3 A The feeder current (FLC_feeder) is the sum of the FLCs of all motors: FLC_feeder = 28.4 A + 18.2 A + 11.3 A = 57.9 A
NEC Requirements (430.6, 430.24, 430.150, 310.16)
430.6(A)(1)
Motor circuit conductors shall have an ampacity not less than the motor FLC.
430.24
Continuous-duty motor loads shall have branch-circuit conductors with an ampacity not less than 125% of the motor FLC.
430.150
Conductors run in raceways or cables with other conductors shall have an ampacity not less than the derated value.
310.16
For conductor terminations rated 75°C or lower, the ampacity of conductors shall be derated 80%.
Conductor Derating (310.16)
Since the conductor terminations are rated at 75°C, we need to derate the feeder current by 80%. Derated feeder current = FLC_feeder x 0.8 = 57.9 A x 0.8 = 46.32 A
Conductor Selection (430.250 FLC Chart)
* Using the NEC 430.250 FLC chart for conductors rated at 75°C and ambient temperature of 30°C, the minimum size XHHW-2 conductor with an ampacity of 46.32 A is
4 AWG.Therefore, the minimum size XHHW-2 feeder circuit conductors required to supply the motor load is 4 AWG, as stated in the answer. Flag for review