Topic: Ground Fault on Large Switch Gear

User: electrical chick, Location: Maryland

Asked on: Friday, January 28, 2011 at 10:21 am EST
Answered on: Tuesday, May 14, 2024 at 12:53 am EDT

Question: We service industrial companies with large 2000 to 4000 amp switch gear. Of these companies, several are plastic extrusion plants. All large switch gear is required to have Ground Fault protection. The problem that some of our customers are having is that any small short downstream trips the main in the switch gear and shuts down the extrusion line or the plant. This causes thousands of dollars of down time and clean up or wasted product. Why do the individual breakers serving these down the line pieces of equipment not trip instead of the main? Is it a series versus fulling rated issue? It is because the AIC rating of subpanels is lower than that of the main switch gear, or is it totally due to the sensitivity of the ground fault protection in the main versus the sensitivity of branch panels and breakers? Can this problem be stopped without violating code or endangering employees? I am trying to fully understand where the problem is before offering a possible solution.

Reasons for Main Breaker Tripping Instead of Subpanel Breakers



Series versus Fulling Rated

- In a series-rated system, the ground fault protection device at the main switchgear trips the entire system, including the subpanels, if any ground fault occurs downstream.- This is because the ground fault current travels through the entire system before reaching the subpanel breakers, causing them to trip only after the main breaker.


AIC Rating Issue

- Arcing Current (AIC) rating indicates the maximum amount of current that a panel or breaker can handle in the event of a short circuit or ground fault.- If the AIC rating of the subpanels is lower than that of the main switchgear, it may not be able to withstand the current and will trip prematurely.

Ground Fault Sensitivity

- The sensitivity of ground fault protection devices is determined by their trip settings.- If the trip setting of the main switchgear is more sensitive than that of the subpanel breakers, the main breaker will trip first even if the ground fault occurs downstream.

Possible Solutions without Violating Code or Endangering Employees



Upgrade Subpanel AIC Rating

- Ensure that the AIC rating of the subpanels is equal to or greater than that of the main switchgear to prevent premature tripping.

Adjust Ground Fault Trip Settings

- Coordinate the trip settings of the main switchgear and subpanel breakers to ensure that the subpanel breakers trip before the main breaker in case of a downstream ground fault.


Install Selective Ground Fault Protection

- Use selective ground fault protection devices that allow the ground fault current to be selectively isolated to the affected subpanel without tripping the main breaker.

Consider Ground Fault Detection and Isolation Systems (GFDI)

- GFDI systems can detect and isolate ground faults without tripping the main breaker, reducing downtime and potential production losses.


Install Interlocked Ground Rods

- Connect ground rods at each subpanel and interlock them to ensure that a ground fault at any subpanel does not affect the main ground.*

Improve Grounding System Maintenance:
- Regularly inspect and maintain the grounding system, including the main ground and subpanel grounds, to ensure optimal performance. Flag for review