User: bwyllie, Location: MA
Asked on: Friday, January 28, 2011 at 10:30 am EST
Answered on: Tuesday, May 14, 2024 at 12:53 am EDT
Question: Using 220.84 I have a load of 700A for a residential riser, am I ok to use a 800A breaker to feed this riser or do I need to goto a 1000A circuit breaker and riser for the 80% rating (or 100% rated 800A breaker). I think 800A would be fine as a residential load is not continuous, but interested in what others think.
80% Rule for Non-Continuous Loads
For non-continuous loads, such as residential loads, which are not expected to operate at maximum capacity for extended periods, the National Electrical Code (NEC) allows for an 80% derating of the breaker. This means that a breaker can be sized to handle 80% of the maximum load.
Calculations
Load: 700A 80% Rule: 700A x 0.80 = 560A
Breaker Selection
Based on the calculations above, a
800A breaker would be sufficient to feed the 700A residential riser, assuming the load is non-continuous.
Reasons for Using an 800A Breaker
NEC Compliance
A 800A breaker complies with the 80% rule for non-continuous loads.
Safety Margin
An 800A breaker provides a reasonable safety margin for potential load fluctuations or future increases.
Cost-effectiveness
An 800A breaker is generally less expensive than a 1000A breaker.
Considerations for Using a 1000A Circuit Breaker
If there is any doubt about the continuity of the load or future load increases. If the residential riser is expected to serve a large or complex structure with multiple high-demand appliances. If 100% rated breakers are preferred for maximum reliability.
Conclusion:
Based on the provided information, using an 800A breaker to feed a 700A residential riser is acceptable and compliant with the NEC, assuming the load is non-continuous. However, if there are concerns about load continuity or future load increases, a 1000A circuit breaker and riser may be more appropriate. Flag for review