Topic: Size #18 AWG Switch Leg???

User: bvano1983, Location: El Paso, TX

Asked on: Friday, January 28, 2011 at 11:25 am EST
Answered on: Tuesday, May 14, 2024 at 12:54 am EDT

Question: I'm working in an elementary school changing out ballasts and yesterday noticed that one of my 2 switch legs going into a 4 lamp fluorescent fixture is a size #18 and the other is a #12. Table 310.5 shows that the minimum size is a #14. Why and when is this #18 permitted to be used?Fixture: 4 Lamp Fluorescent w/ 2 BallastsConduit: 1/2" EMTConductors entering fixture: #12 Red, #18 Black, #12 Green, #12 White.

The use of a #18 conductor as one of the hot legs in a 4-lamp fluorescent fixture is permitted under the following conditions

NEC Section 410.21(B)(1)

allows for the use of smaller conductors for portions of a branch circuit within luminaires, provided that: The conductors do not extend beyond the luminaire. The ampacity of the conductors is sufficient for the load supplied.In this case, the #18 conductor is used within the fixture to connect one ballast to the hot lead (#12 Red). The load on this conductor is limited to the current draw of the single ballast, which is typically well below the ampacity of a #18 conductor.Therefore, the use of a #18 conductor in this application is permitted under the NEC. Flag for review