Topic: Computer power supply in a Class II, Div. 2 space

User: BigMike, Location: Mission Viejo, CA

Asked on: Friday, January 28, 2011 at 12:00 pm EST
Answered on: Tuesday, May 14, 2024 at 12:54 am EDT

Question: I have a computer rated for a classified environment. It's just like any other computer, except the power supply is external to the computer. (Similar to a laptop) The computer needs to be installed in the classified space and is over 100' from an unclassified area. Can I put the power supply in a Nema 4 enclosure? If so, what about the 120V receptacle inside the Nema 4 enclosure? Does it need to be rated for a Class II, Div. 2 area?My idea is to route threaded IMC conduit with 120V to the N4 enclosure. Install a standard 120V receptacle in the enclosure and place the power supply inside the enclosure. Then route the 24VDC cable on the output of the power supply, through IMC conduit, to the threaded connection on the computer. Anyone see problems with this?Thanks.

Power Supply Placement in Nema 4 Enclosure

Yes, you can place the external power supply in a Nema 4 enclosure. Nema 4 enclosures are designed to protect electrical equipment from water, dust, and other environmental hazards.

Receptacle in Nema 4 Enclosure

The 120V receptacle inside the Nema 4 enclosure does

not
need to be rated for Class II, Div. 2 areas. This is because the enclosure itself provides the Class II, Div. 2 protection.

Conduit Routing and Cabling

Your plan to route threaded IMC conduit with 120V to the Nema 4 enclosure, install a standard 120V receptacle, and then route the 24VDC cable to the computer is acceptable.

Additional Considerations

Ensure that the conduit is properly sealed at all connection points to maintain the Class II, Div. 2 protection. Use Class II or Class III rated cable for the 120V and 24VDC cables. Consider providing an additional level of protection by using a surge protector or UPS to protect the power supply and computer from voltage fluctuations. Mount the Nema 4 enclosure in a convenient location for maintenance and access. Label the enclosure clearly to indicate that it contains classified equipment.

Specific Codes and Standards:


Please refer to the following codes and standards for specific requirements:
NFPA 79: Electrical Standard for Industrial Machinery NFPA 800: Standard for Electric Generating Plants ANSI/UL 50: Enclosures for Electrical Equipment (NEMA and IEC) Flag for review