Topic: Grounding Electrode for Multiple Separately Derived Systems - NEC 250.30A4

User: tombrinson, Location: maryland

Asked on: Friday, January 28, 2011 at 12:05 pm EST
Answered on: Tuesday, May 14, 2024 at 12:54 am EDT

Question: Our firm commonly uses the method described in NEC 250.30A4 to ground multiple dry type transformers in larger buildings (i.e. schools, large commercial offices) as follows:From the equipment ground bar in the main switchboard (MSB) we route a 3/0 copper conductor, looped around the building, to ground plates in each electrical room.The plates are typically 1/4"x4"x12" copper. From the plate to the Xo bar in the transformer a grounding electrode conductor, based on 250.66, is installed using a crimp type connector.My questions are:1. Can the 3/0 conductor be "looped" (i.e. terminated with crimp connectors) in and out from room to room? Or does it have to be continuous?2. Can it routed multiple runs, (i.e. from the MSB to each electrical room) within the same building or does it have to be a continuous loop?

1. Can the 3/0 conductor be "looped" (i.e. terminated with crimp connectors) in and out from room to room? Or does it have to be continuous?

No, the 3/0 conductor cannot be "looped" in and out from room to room using crimp connectors. The NEC requires that this grounding conductor be continuous from the equipment ground bar in the main switchboard (MSB) to each transformer's grounding electrode system (250.30A4). This means that you cannot terminate the conductor with crimp connectors in and out of each room.2. Can it be routed multiple runs, (i.e. from the MSB to each electrical room) within the same building or does it have to be a continuous loop?

The NEC does not specifically address whether the grounding conductor can be routed in multiple runs within the same building. However, the intent of the NEC is to provide a continuous, low-impedance path to ground for the transformers. Routing the grounding conductor in multiple runs could increase the impedance of the path and reduce the effectiveness of the grounding system. For this reason, it is recommended to route the grounding conductor as a continuous loop from the MSB to each transformer's grounding electrode system. Flag for review

Previous Question Next Question