User: stuartdmc, Location: Newport Beach, Irvine, CA
Asked on: Friday, January 28, 2011 at 3:24 pm EST
Answered on: Tuesday, May 14, 2024 at 12:54 am EDT
Question: Is it true that you may max out the main circuit breaker to 100% if the LCL and LML are taken in account?For example: I have a 200a 1 phase 120/240v 42 space panel the connected loads total 140 amps with all LCL and LML taken in account, being a restaurant I?ve taken the demand factor for cooking equipment and now the total 1phase load is 109 amps. The main circuit breaker feding the panels is 125 amps. Is this allowed?Is the 125 amp main adequate?
No, it is not true that you may max out the main circuit breaker to 100% if the LCL and LML are taken into account.According to the National Electrical Code (NEC), the maximum demand factor for lighting and receptacle loads in a restaurant is 75%, not 100%. This means that you can only use 75% of the calculated load when sizing the main circuit breaker.In your example, the total 1-phase load is 109 amps. Using a demand factor of 75%, the adjusted load is 109 amps x 0.75 = 81.75 amps.Since the main circuit breaker feeding the panels is 125 amps, it is adequate for the load. Flag for review