Topic: Waveguide in other spaces used for environmental air (plenum)

User: encoreman, Location: Austin, TX

Asked on: Friday, January 28, 2011 at 6:24 pm EST
Answered on: Tuesday, May 14, 2024 at 12:55 am EDT

Question: I have to run some waveguide in other spaces used for environmental air (plenum). The waveguide is not available as plenum rated. Someone suggested this product:http://www.thermalceramics.com/pdfs-uploaded/brochureseurope/FireProtection.pdfspecifically, PlenumWrap.In reading the 300.22(C) of the 2011 code, I can't see where is allows or disallows the use of PlenumWrap type products.Help!Jack

2011 NEC Section 300.22(C) Plenum Cables and Wires> "(C) Other Cables and Wires. Other cables and wires installed in a plenum shall be listed as having adequate fire-resistant and low smoke-producing characteristics."Interpretation

The cited code section requires that cables and wires installed in a plenum be listed as having adequate fire-resistant and low smoke-producing characteristics. PlenumWrap is a product designed to provide fire resistance and reduce smoke production. However, it is not a cable or wire.The code does not specifically address the use of PlenumWrap or similar products to protect non-plenum-rated cables and wires installed in a plenum.

Recommendations

To ensure compliance with the code, it is recommended that you consult with the local authorities having jurisdiction (AHJ). The AHJ may allow the use of PlenumWrap or similar products, provided that they can be demonstrated to provide adequate fire resistance and low smoke production.

Possible Options



Obtain a field listing

Contact an approved testing laboratory to have the waveguide wrapped with PlenumWrap and tested for fire resistance and low smoke production. If the waveguide passes the test, it may be considered as having adequate fire-resistant and low smoke-producing characteristics.


Use alternative plenum-rated waveguide

Explore the possibility of using waveguide that is specifically rated for use in plenum spaces.*

Isolate the waveguide:
Install the waveguide in a separate enclosure that is sealed from the plenum space. The enclosure should be designed to prevent the spread of smoke and fire in the event of a cable or wire failure. Flag for review