User: mpd, Location: Tennessee
Asked on: Friday, January 28, 2011 at 7:56 pm EST
Answered on: Tuesday, May 14, 2024 at 12:55 am EDT
Question: looking for some opinions, thanks in advance,230.40 exc. 5 permits a second of service entrance conductors to supply supply systems covered in 230.82 (6) (PV systems)230.71 (A) permits the service disconnecting for each set of service entrance conductors permitted by 230.40 exc. 5 (PV systems)would it be permitted to tap the line side of the service disconnecting means and have up to six service disconnects for the PV service entrance conductors & the house service entrance conductors at different locations, but the service disconnects for each service entrance would be grouped or must the PV service disconnect & house service disconnect be grouped at the same location
Permitted
Yes, it is permitted to tap the line side of the service disconnecting means and have up to six service disconnects for the PV service entrance conductors and the house service entrance conductors at different locations.
Code References
230.40 Exception 5
Allows a second set of service entrance conductors to supply PV systems.
230.71(A)
Permits a service disconnecting means for each set of service entrance conductors permitted by 230.40 Exception 5 (PV systems).
Conditions
The service disconnects for each service entrance must be grouped or located at the same location. The service entrance conductors for each service entrance must be sized accordingly. The service disconnecting means must be clearly labeled to identify the circuits it controls.
Rationale
Isolating each service entrance with a separate disconnecting means allows for safe maintenance and troubleshooting of the PV system and the house electrical system. Grouping or locating the service disconnects at the same location provides easy access for service personnel and reduces the potential for confusion.
Additional Considerations: The maximum number of service disconnects may be limited by local codes or utility requirements. The service equipment must be installed in accordance with the manufacturer's instructions and applicable code requirements. It is recommended to consult with a qualified electrician or AHJ to ensure compliance with all applicable codes and standards. Flag for review