Question: Ive just started at this new job and doin a rough in with a simple 350 amp single phase 120/240 v service my boss says "my bonding jumper needs to be bugged outside to the GEC " . i said ive never done that before . ive always gone from the terminal bar of 200 a to 150a its says accesible right . i would think that would be a better gf return path. just what to here what others think
Bonding Jumper to GEC
Your boss is correct in requiring a bonding jumper from the bonding terminal bar in the panel to the grounding electrode conductor (GEC). This is a requirement of the National Electrical Code (NEC) and is intended to provide a low-impedance path for ground fault currents to flow back to the source.
Accessible Bonding Location
While the bonding jumper can be connected to the panel's bonding terminal bar, it is typically recommended to extend it outside the panel to the GEC for several reasons: Enhanced Grounding
Connecting the bonding jumper directly to the GEC provides a more reliable grounding connection than relying on the internal ground bus of the panel.
Reduced Voltage Potential
In the event of a ground fault, the voltage potential on the panel's enclosure is reduced by connecting the bonding jumper to the GEC.*
Simplification of Inspections
It is easier to inspect and ensure proper bonding when the jumper is visible and accessible outside the panel.
Ground Fault Return Path
While the bonding jumper also serves as a ground fault return path, it is important to note that the preferred return path for ground fault currents is through the equipment grounding conductors (EGCs). The bonding jumper is intended to provide a supplementary path in case the EGCs are compromised.
Conclusion
Based on the NEC requirements and industry best practices, it is recommended to install a bonding jumper from the bonding terminal bar in the panel to the GEC outside the panel. This provides a reliable and safe ground fault return path and enhances the overall grounding system of the electrical installation. Flag for review