Question: How do you size the OCPD with a VFD converting 240V single phase to three phase, for a 3-phase 15hp motor?42A @ 240V, 3-phaseMy thought:Convert 42A to KVA, then convert KVA to 240V, 1-phase amps = 72.7A72.7 * 2.5 = 180A (max).
Step 1: Convert 3-phase Amps to KVA
KVA = √3 V I PFWhere: KVA = kVA rating V = voltage (240V in this case) I = current (42A in this case) PF = power factor (assumed to be 0.8 for induction motors)KVA = √3 240V 42A 0.8 = 20.2kVAStep 2: Convert KVA to 1-Phase Amps
Amps = KVA / VWhere: Amps = 1-phase amps KVA = kVA rating (20.2kVA in this case) V = voltage (240V in this case)Amps = 20.2kVA / 240V = 84.1AStep 3: Multiply by OCPD Derating Factor
For VFDs powering induction motors, the NEC requires an OCPD derating factor of 2.5.OCPD = Amps Derating FactorOCPD = 84.1A * 2.5 = 210.25ANote:
The calculated OCPD value should be rounded up to the next standard fuse or circuit breaker size. In this case, you would select a 225A OCPD. Flag for review