Question: I have three individual IT server racks, on wheels not bolted down, that are not grounded to the GES. Within this small IT room is a distribution panel and x-former. The xf is grounded properly, including building steel, as well as the panelboards. My question is: Can the IT racks be grounded by simply running a #6 copper to any ground bus within these panelboards, or do I have to hit the bldg steel as well, or may I just use the bldg steel, or am I missing something? 645.15 talks about grounding this equipment, built in UPS aside, but I cannot find the minimum requirements without interpretation. Need a solid reference. Thanks in advance.Jazer
Requirements for Grounding IT Server Racks
NEC 645.15(B): "Equipment Enclosures Associated with Electrical Installations Other Than Service Equipments shall be grounded in accordance with 250.134." NEC 250.134(A)(1): "Metal equipment enclosures shall be grounded by a metal equipment grounding conductor run with circuit conductors and connected to the system grounding conductor or the grounding bus in the equipment."Grounding Methods
Option 1
Run a #6 copper conductor from each IT rack to the grounding bus in the distribution panel.
Option 2
Run a #6 copper conductor from each IT rack to the building steel.
Option 3
Run a #6 copper conductor from each IT rack to both the grounding bus and the building steel.
Recommended Practice
Option 3 is the most comprehensive and recommended grounding method for IT server racks. Grounding to both the distribution panel and the building steel provides multiple paths for fault current to return to the source, enhancing safety and reducing the risk of electrical shock.
References: [NEC 645.15](https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70)* [NEC 250.134](https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70) Flag for review