Topic: Roadway decorative lights with GFCI outlet

User: chriskthx, Location: Raeford, NC

Asked on: Sunday, January 30, 2011 at 3:53 pm EST
Answered on: Tuesday, May 14, 2024 at 12:58 am EDT

Question: Does anyone have any recommendations on calculation of voltage drop for 200W decorative lights with a GFCI outlet attached on them to the same circuit? I assume they will be used to place Christmas lights or decorations.This is the first time I've come across a request of placing outlets on the poles. My initial thought is to just assume that 100W would be connected to the outlet and run the calcs with that, however I am curious if anyone else has opinions or has worked with this before.

Voltage Drop CalculationCircuit Parameters

Power consumption: 200W Voltage: 120V Wire length: Assume 100ft (round trip) Wire gauge: #14 AWG

GFCI Outlet Factor

A GFCI outlet adds negligible resistance to the circuit (less than 0.1 ohms). For simplicity, it can be ignored in the calculation.

Wire Resistance

Resistance of #14 AWG wire is 0.0041 ohms per foot. Total wire resistance: 0.0041 ohms/ft x 100ft x 2 (round trip) = 0.82 ohms

Voltage Drop

Voltage drop = Current x Resistance Current = Power / Voltage = 200W / 120V = 1.667A Voltage drop = 1.667A x 0.82 ohms =

1.36V
Conclusion

The voltage drop for the 200W decorative lights with a GFCI outlet attached on the same circuit over 100ft of #14 AWG wire is approximately 1.36V. This voltage drop is considered acceptable and within the typical range for residential lighting circuits.

Additional Considerations:
If the wire length is longer than 100ft, the voltage drop will increase proportionally. If the power consumption is higher than 200W, the voltage drop will also increase.* It is always recommended to check the manufacturer's specifications for the maximum voltage drop allowed for the decorative lights. Flag for review