User: Alwayslearningelec, Location: NJ
Asked on: Monday, January 31, 2011 at 10:33 am EST
Answered on: Tuesday, May 14, 2024 at 12:59 am EDT
Question: I am trying to find out howm many FSD's I can put on a 208v ckt. They are not shown on the electrical floorplans, only on the panels schedule and they show (4) 20a ckts for them. There are (90) on the mechanicals. How can I figure the connected load or how many i can put on one ckt. I looked on the mech schedules for info on the fsd's but don't see any. Thanks very much.
Determining Connected Load and Maximum Number of FSDs on a 208V CircuitStep 1: Electrical Panel Schedule The panel schedule indicates that there are four 20A circuits for FSDs. This means that the maximum available current for FSDs is 4 x 20A = 80A.
Step 2: Connected Load Calculation Since the connected load for FSDs is not provided on the electrical floorplans, you need to estimate it. A typical FSD may draw around 0.5A to 1.5A of current. Assuming an average current draw of 1A per FSD, the total connected load would be: 90 FSDs x 1A/FSD = 90A.
Step 3: Comparison to Available Current The total connected load (90A) exceeds the available current (80A) on the four 20A circuits. Therefore, you cannot connect all 90 FSDs on a 208V circuit.
Maximum Number of FSDs per Circuit To determine the maximum number of FSDs that can be connected to one circuit, use the following formula:
Number of FSDs = Available current (A) / Current draw per FSD (A)* Assuming a current draw of 1A per FSD, the maximum number of FSDs per circuit is:Number of FSDs = 20A / 1A = 20 FSDsConclusion