Topic: Ground rod required in detached garage?

User: richwaskowitz, Location: Shelby Twp. MI, near Detroit

Asked on: Monday, January 31, 2011 at 12:06 pm EST
Answered on: Tuesday, May 14, 2024 at 12:59 am EDT

Question: I just can't be sure whether a ground rod is required at this detached garage or not. Please cite the specific article.1. Residential detached garage2. No piping of any kind in the garage3. Underground feed from house main panel via a 30 amp 2 pole breaker at 120/240 volts4. Equipment ground and neutral is provided to 4 circuit sub-panel where neutral is isolated from groundDo I install a ground rod and bond the neutral at the garage and not use the equipment ground in the feeder? Or do I treat this as I would a sub-panel within the house (provide an isolated neutral)?

NEC 250.30(A)(1) states that a grounding electrode conductor shall be connected to the grounding electrode system, and shall be connected to the system grounding conductor, if of sufficient size; or to a grounding electrode conductor run with the circuit conductors.

NEC 250.58(A) requires a grounding electrode system to be installed for detached structures that shall be connected to the grounding electrode conductor at the building or structure.

Based on the information provided, a ground rod is required at the detached garage. Flag for review