Topic: Fault Current

User: brian john, Location: Leesburg, VA

Asked on: Monday, January 31, 2011 at 3:46 pm EST
Answered on: Tuesday, May 14, 2024 at 1:00 am EDT

Question: I received a call today regarding a site where the contractor furnished and install all the distribution equipment. Problem was no coordination study was performed. Long story short they had some tripping issues and decided to perform a coordination study. As part of the study it was found all Switchgear exceeds available fault current, but the 480 VAC distribution panels rated 25,000 AIC do not meet the available fault current of 40,000 A.This contractor that I do work for is searching for answers. My answer was new panels. He was told by another contractor that installing current limiting fuses would do the trick. And?Any thoughts would be appreciated.

Current Limiting Fuses

Current limiting fuses may be an option to reduce the fault current seen by the distribution panels, but there are several considerations: Fuse Selection

The fuses must be carefully selected to ensure they will limit the fault current to a level below the panel's rating. Improper fuse selection can lead to ongoing tripping issues or worse, damage to the equipment.


Fuse Costs

Current limiting fuses can be expensive, especially for high-amperage applications.

Limitations

Fuses can only clear faults after они occur, which can result in momentary power interruptions or equipment damage.


Future Expansion

If the facility requires expansion or additional loads in the future, the fuse size may need to be increased to accommodate the higher fault currents.

New Panels


Installing new distribution panels with a higher AIC rating is a more reliable and permanent solution. It ensures that the panels are rated for the available fault current and eliminates the risk of premature tripping or damage.

Other Considerations Upstream Protection

The switchgear that feeds the distribution panels must also be evaluated to ensure it can handle the available fault current.


Coordination Study

A revised coordination study should be performed after any changes are made to ensure that the entire electrical system is properly protected.*

Contractor's Responsibility

The contractor who installed the equipment is ultimately responsible for ensuring that it meets the requirements of the electrical code and industry standards. They should work with a qualified electrician to determine the best solution for this situation.Based on the information provided,

installing new panels with a higher AIC rating
is the recommended solution. Current limiting fuses may be considered as a temporary measure, but they should be carefully selected and managed to ensure the safety and reliability of the electrical system. Flag for review