User: bigglad, Location: Cleveland Ohio
Asked on: Tuesday, February 1, 2011 at 12:02 pm EST
Answered on: Tuesday, May 14, 2024 at 1:01 am EDT
Question: I have a customer who wants me to install a 600 amp 3-phase circuit breaker in a NEMA 4 Steel enclosure, for a service.My question is...Is this (and any other service MCB/Fuse) supposed to be service rated equipment.AIC ratings is another question later.Thanks
Yes, a 600 amp 3-phase circuit breaker installed in a NEMA 4 Steel enclosure for a service should be service rated equipment.The National Electrical Code (NEC) requires that service equipment, including circuit breakers and fuses, be service rated. Service rated equipment is designed to withstand the high fault currents that can occur on a service entrance.The NEC defines service rated equipment as equipment that is suitable for use as service equipment. Service equipment is defined as the equipment that is located at the point of connection between the utility and the customer's premises.The NEC also requires that service equipment be able to withstand the available fault current at the point of connection. The available fault current is the maximum amount of current that can flow through a fault at the point of connection.Circuit breakers and fuses that are not service rated may not be able to withstand the high fault currents that can occur on a service entrance. This could result in a dangerous situation, such as an electrical fire.Therefore, it is important to use service rated equipment for all service applications. Flag for review