Question: I have an electric hot water heater that had a wire burn up about 4 inches of insulation off the conductor because of a loose connection on the element. Would I be in violation of the code to splice the conductor in the element wiring compartment?
Yes, it would be a violation of the National Electrical Code (NEC) to splice the conductor in the element wiring compartment of an electric hot water heater.NEC Requirements
Article 422.14(C)(4)
Connections between the element wiring compartment and the branch-circuit terminals must be made without splices or taps.
Article 110.14(C)
"Splices and taps shall be made only in junction boxes, outlet boxes, or other enclosures designed for such use."
Reasoning
The element wiring compartment is a sealed and hazardous area where water and heat are present. Splicing conductors in this location poses the following risks:
Electrical shock
If the splice is not properly insulated, it could create an electrical hazard.
Fire
If the splice overheats, it could ignite the insulation or surrounding materials.
Reduced reliability
Splices are less reliable than continuous conductors and can introduce points of failure.
Solution
To repair the damaged wire, you should:
Turn off power to the water heater before starting any work. Remove the element from the water tank. Replace the damaged element with a new one. Install a new element wiring compartment gasket. Reassemble the water heater.Note: It is recommended to have a qualified electrician perform these repairs to ensure that they are done safely and in accordance with the NEC. Flag for review