User: speck1, Location: Lockport, IL
Asked on: Tuesday, February 1, 2011 at 4:52 pm EST
Answered on: Tuesday, May 14, 2024 at 1:02 am EDT
Question: I have a 600A overcurrent device on a long feeder run. Per 250.0122 it would require a #1cu ground before any adjustment for voltage drop. I am running 3 sets of 350kcmill to accomidate for voltage drop. When I calculate what the revised ground should be using the example from the handbook 250.122, B the answer does not seen correct to me.Example 1600A conductor per 310.16 = 1500 kcmill3*350kcmill conductors = 1050 kcmill1050/1500 = .7I take this to mean that even tho I up sized the current carring conductiors the ground does not need to upsized?Example 2But if you use 2 set of 350's as your starting point the calculation becomes1050/700= 1.5 which directs you to a 2/0 groundExample 3Or if you use 4 sets of 1/0 you get1050000/422400 = 2.4 which directs you to a 4/0 groundCan this be correct that by the tables in the code (using 1500kcmill) the ground does not need to be upsized in this case?And what about is changing depending on how you parallel it?
Example 1
Your calculation is incorrect. The revised ground size should be 1/0 AWG.1. Determine the ground size for the original conductor size (1500 kcmil): 1500 kcmil / 1000 = 1.5 AWG (between 2/0 AWG and 4/0 AWG)2. Multiply the ground size for the original conductor size by the ratio of the parallel conductor ampacity to the original conductor ampacity: 1.5 AWG x (1050 kcmil / 1500 kcmil) = 1.05 AWG (between 1/0 AWG and 2/0 AWG)3. Round up to the nearest standard AWG size: 1/0 AWG
Example 2 and 3
Your calculations are correct. However, they illustrate that the ground size can vary depending on the number of parallel conductors used.
Conclusion:
Yes, the ground size can vary depending on the size and number of parallel conductors used. The ground should be sized using the method outlined in 250.122(B), which takes into account the ampacity of the current-carrying conductors.In this case, the ground size does not need to be upsized because the revised ampacity of the parallel conductors exceeds 1500 A. However, if you were to use a smaller number of parallel conductors, the revised ampacity would be lower and you would need to upsize the ground. Flag for review