User: John McKellar, Location: New York
Asked on: Tuesday, February 1, 2011 at 5:45 pm EST
Answered on: Tuesday, May 14, 2024 at 1:02 am EDT
Question: Is there a code section that would not allow a 8 foot light fixture with two ballast, each ballast feed from a 20 amp single pole breaeker in different sub panels? The reason is the owner wants to stage is transfer switches so that only half the lighting is on when gen. first starts and bring the rest of the lighting later. Thank you.
National Electrical Code (NEC)Section 240.15(B)(5)Explanation
This section of the NEC prohibits connecting multiple circuits from different panelboards to supply the same load. In this case, each ballast is powered from a different subpanel, violating this rule.Therefore,
the proposed configuration is not allowed by the NEC. Flag for review