Question: What is the formula to find out what the amperage of a 30kw heater, 3 phase at 120/208 volts would be

The formula to calculate the amperage of a 30kW heater, 3 phase at 120/208 volts is:

Amperage = Power / (Voltage  √3)
Where: Power is in watts (W) Voltage is in volts (V) √3 is the square root of 3, which is approximately 1.732Plugging in the given values:
Amperage = 30,000 W / (120 V * 1.732)
Amperage ≈ 136.3 A
Therefore, the amperage of a 30kW heater, 3 phase at 120/208 volts is approximately 136.3 A. Flag for review