User: DavidA, Location: Fresno, CA
Asked on: Wednesday, February 2, 2011 at 1:01 pm EST
Answered on: Tuesday, May 14, 2024 at 1:04 am EDT
Question: A customer has a number of 3/4" PVC stub ups inside a building with a 6" cement slab. Originally these conduits were for floor mounted open case coolers for produce etc. Now the customer wants floor receptacles in place of the stub ups as the equipment is no longer going to be used. Rather than using a jack hammer to chip around each conduit, how about core drilling a hole slightly larger than the floor box at each location, cutting the conduit down and droppping the box right on top? Any other ideas or products that might help?
Core Drilling Method
Core drilling a hole slightly larger than the floor box is a feasible solution. To prevent the box from dropping too far, use a spacer between the box and conduit. Seal around the hole and box with a suitable sealant to prevent water and debris ingress.
Alternative Ideas and Products
Conduit Extender
Use a conduit extender to connect the remaining conduit to the floor box. This avoids drilling or chipping the slab.
Flush Floor Box
Consider using a flush floor box that sits level with the finished floor. This eliminates the need for drilling or cutting the conduit.
Floor Plate with Cord Pass-Through
Install a floor plate with a cord pass-through. This allows power cords to be plugged in from above without drilling or cutting the conduit.
Concealed Electrical Raceway
Run the new electrical wiring through a concealed raceway under the flooring. This requires some minor cutting and installing of the raceway, but it provides a clean and less invasive solution.
Additional Tips: Before drilling or cutting, locate and mark all existing conduits and utilities to avoid damage. Protect the finished flooring from debris and damage during drilling and cutting. Use a sharp hole saw or core drill bit for clean and precise holes.* Double-check the box dimensions and hole size to ensure a proper fit. Flag for review