Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Separation of Services conductors

User: Red Wiggler

Asked on: Wednesday, February 2, 2011 at 1:01 pm EST
Answered on: Tuesday, May 14, 2024 at 1:04 am EDT

Question: I have a project that has an existing 4160 volt switchboard in an electric room. We are adding an additional switchboard that will have a separte incoming service and will be installed in a line with the existing board. The existing installation uses a common concrete raceway underneath the switchboard and this raceway will extend under the new board as well. The load conductors are leaving both boards in aluminum rigid conduit. All load conductors leave the building at one end of the concrete raceway. (24" x 24" x 30' raceway dimensions).The incoming services enter the exisiting concrete raceway is in the middle of the concrete gutter to form a "T". The incoming conductors on the existing board are run "open" in the concrete gutter (raceway). They are not fire taped or protected by anything. When I install the "new" service conductors... am I required to provide some sort of separation between the two services? Would fire tapping be a solution?

NEC Requirement for Separation of Services

Article 300.3(B) of the National Electrical Code (NEC) requires that services shall not occupy the same spaces except where separated by a permanent barrier with a minimum fire resistance rating of 1 hour or by a vertical distance of 6 feet between energized parts.

Applicability to Your Situation

In your case, the existing and new services are installed in the same concrete raceway, which does not provide the required separation. Therefore, you are required to provide an acceptable means of separation.

Fire Taping as a Solution

Fire taping can be used to provide separation between the services. Fire tape is a self-adhering, intumescent material that expands when exposed to heat, creating a fire-resistant barrier.To use fire tape in this application, you would wrap it around the conductors of the new service where they enter the concrete raceway. This would create a fire-resistant barrier that separates the new service from the existing service.

Other Separation Methods

In addition to fire taping, other acceptable methods of separation include: Installing a metal barrier with a fire resistance rating of 1 hour within the concrete raceway Running the new service conductors in a separate concrete raceway or conduit Maintaining a vertical distance of at least 6 feet between the energized parts of the two servicesRecommendation

Based on the information provided, it is recommended that you use fire taping to separate the existing and new services in the concrete raceway. This would be a cost-effective and efficient solution to meet the NEC requirement.

Additional Considerations
Ensure that the concrete raceway is adequately sized to accommodate the additional conductors. Verify that the fire tape used is suitable for the specific type of cable installation. Comply with all applicable local code requirements. Flag for review

Previous Question Next Question